240V stepped down to a 120 leg |
Post Reply | Page <12 |
Author | ||
JStrube
Groupie Joined: 11 Aug 2014 Location: Atwater, CA Online Status: Offline Posts: 90 |
Topic: 240V stepped down to a 120 leg Posted: 18 Nov 2014 at 6:58pm |
|
You could put a sub panel out at the well & have one run to it, but it would have to be 4 wire. Still need that neutral.
|
||
2012 181G
|
||
Luv2Q
Senior Member Joined: 30 Aug 2014 Location: Central TX Online Status: Offline Posts: 309 |
Posted: 18 Nov 2014 at 7:12pm | |
But where do I connect the neutral at the pump switch? I only have two posts (both hot) + a ground post to connect to. Reason for my question: I've seen houses wired with 2 hots and a ground coming into the main service panel. The subpanel idea looks like the same thing but on a smaller scale. No?
|
||
John & Teri
Tundra 5.7L V8 / RP 180 E2 WDH / Integrated controller (POS) replaced by Tekonsha P3 |
||
techntrek
Admin Group - pHp Joined: 29 Jul 2009 Location: MD Online Status: Offline Posts: 9059 |
Posted: 18 Nov 2014 at 7:22pm | |
Something that is a problem no matter what you do, the pressure switch is inside, so the wires running to the well aren't connected unless the well is running.
There are so many things you would have to do to make this safe and to code it will be far easier to just run a new 10 gauge underground-rated line out to the pod. Won't be cheap though.
|
||
Doug ~ '10 171 (2009-2015) ~ 2008 Salem ~ Pod instruction manual
|
||
CharlieM
Senior Member Joined: 23 Nov 2012 Location: N. Colorado Online Status: Offline Posts: 1797 |
Posted: 18 Nov 2014 at 7:55pm | |
Caution here. What I suggested was to install a separate 30A breaker in you main panel, not the well pump box. You cannot develop the neutral at the present pump. You must go all the way back to the main service entry at the house. Of the three wires coming from the power pole, two are hot and one is the neutral. This neutral is connected to a ground stake and ground buss at the main power panel and only there. The neutral and ground must be kept separate from there out to any using devices including sub panels. For 120V circuits you must carry neutral, hot, and ground separately. So you must run the 3 wires from the camper or sub panel all the way back to the main house panel, not the well house. On a separate subject, upping the breakers that feed the well from the main panel may not be possible. The breakers are sized to protect the wire to the well pump, not the pump. Fifty Amp breakers would require #6AWG if using copper UF direct burial wire; 60 Amps requires #4. I would stay with a new 30A breaker and run at least #8 wire; #6 if you're really going 100 feet. |
||
Charlie
Northern Colorado OLD: 2013 RP-172, 2010 Honda Pilot 3.5L 4WD PRESENT: 2014 Camplite 21RBS, 2013 Supercharged Tacoma 4L V6 4WD |
||
Luv2Q
Senior Member Joined: 30 Aug 2014 Location: Central TX Online Status: Offline Posts: 309 |
Posted: 18 Nov 2014 at 8:46pm | |
Well, Rats .. Back to the drawing board. But on the pressure switch, the wires going to it are hot regardless of whether the switch is tripped or not. At the hot poles on the switch - which are then connected to my fictional subpanel - it seems like that would be nothing more than a splice. But, it's clear that I'm in over my head. Durn it, wish I understood more. Thanks again for the advice, everybody.
|
||
John & Teri
Tundra 5.7L V8 / RP 180 E2 WDH / Integrated controller (POS) replaced by Tekonsha P3 |
||
techntrek
Admin Group - pHp Joined: 29 Jul 2009 Location: MD Online Status: Offline Posts: 9059 |
Posted: 18 Nov 2014 at 9:43pm | |
If the pressure switch is close by then yes, the wires running from your panel to it would be hot all the time, but as mentioned w/o a neutral you aren't in the ballpark yet.
|
||
Doug ~ '10 171 (2009-2015) ~ 2008 Salem ~ Pod instruction manual
|
||
Buxmont
Newbie Joined: 25 Sep 2014 Location: PA Online Status: Offline Posts: 9 |
Posted: 19 Nov 2014 at 11:23am | |
<span style="line-height: 1.4;">I've seen houses wired with 2 hots and a ground coming into the main service panel. The subpanel idea looks like the same thing but on a smaller scale. No?</span> [/QUOTE]
What you are seeing, if this is the main panel being fed from the utility, and there is a meter (within 10') in-between, is not a ground, it is the Neutral. The Ground is derived from pounding in an 8' rod into the earth. I agree with others, go get #10-2 UF (that is direct bury wire) and run a new single pole circuit to the Pod.
|
||
2015 178 Rpod
2003 Chevy Trailblazer |
||
JStrube
Groupie Joined: 11 Aug 2014 Location: Atwater, CA Online Status: Offline Posts: 90 |
Posted: 19 Nov 2014 at 11:28am | |
It would end at the sub panel. What I heard you ask is that could you install a sub panel at your well, then put breakers there to serve both the well & POD. The answer is yes, if you size everything correctly. You would have a breaker in your main, sized to protect the wire to the sub panel, then in the sub panel, a breaker for the pod & a breaker for the well. The POD breaker would be 30A single pole, the well double pole of whatever size you need. Mine at home is 30A. The neutral would not run to the pump, only the pod. It has been a while since I did my wiring, would have to go back & consult the books to verify exact requirements. I work on the utility side of the electric industry, so that is my area of concentration. As a consequence, I learn quite a bit of the customer side of the meter, enough to seek out the right answers, but not enough to be second nature. Electricity is fun, as long as you keep it in the wires.
|
||
2012 181G
|
||
CharlieM
Senior Member Joined: 23 Nov 2012 Location: N. Colorado Online Status: Offline Posts: 1797 |
Posted: 19 Nov 2014 at 11:59am | |
Correct answer. The neutral has to go to the Pod, but not to the pump itself. The OP doesn't say if the pump/controller is in a well house but carrying the neutral to the pump area would allow for a future light, heat tape, or outlet for tools.
|
||
Charlie
Northern Colorado OLD: 2013 RP-172, 2010 Honda Pilot 3.5L 4WD PRESENT: 2014 Camplite 21RBS, 2013 Supercharged Tacoma 4L V6 4WD |
||
Post Reply | Page <12 |
Forum Jump | Forum Permissions You cannot post new topics in this forum You cannot reply to topics in this forum You cannot delete your posts in this forum You cannot edit your posts in this forum You cannot create polls in this forum You cannot vote in polls in this forum |